I mean no disrespect, but if you have to ask this question, then you should probably be calling an electrician who will be able to safely do this.
If you are referring to house wiring then the answer is no. A breaker protects the wire size that is connected to the breaker. In home wiring most homes are wired with a #14 wire which is rated at 15 amps. That is why the wire is protected by a 15 amp breaker. The correct wire size to connect to a 40 amp breaker is a #8. This size wire is too large to connect to receptacles an light fixture terminals.
No, 10 gauge wire requires the use of a 30 amp breaker. A 20 amp breaker is only used on 12 gauge wire.
A dryer requires a 30 amp receptacle. This will be to receive a four blade dryer plug. The wire needed will be a three copper wire #10 cable set with a bare #14 copper ground wire. The breaker will be a two pole 30 amp breaker.
Use a 30 amp breaker.
For typical residential house wiring 12 AWG wire is required for a 20 Amp breaker. If you change out the breaker for a 25 A breaker you would have to rewire the circuit with 10 AWG. In that case you could up the breaker to 30 Amps. All outlets and switches should be rated at the same voltage and current as the breaker.
6millimeter square.
If you are referring to house wiring then the answer is no. A breaker protects the wire size that is connected to the breaker. In home wiring most homes are wired with a #14 wire which is rated at 15 amps. That is why the wire is protected by a 15 amp breaker. The correct wire size to connect to a 40 amp breaker is a #8. This size wire is too large to connect to receptacles an light fixture terminals.
Depends on the size of the wire going to the A/C. If the wire is AWG #10 you cannot install a 40 amp breaker. If the wire is AWG #8 you can.
Yes, a 20 amp breaker requires AWG # 12 copper wire. A 15 amp breaker requires AWG # 14 copper wire.
Look on the heater and see what amps it is pulling. That will determine the wire size and breaker size. It must be on a dedicated circuit. 15 amps = AWG # 14 wire with 15 amp breaker 20 amps = AWG # 12 wire with 20 amp breaker 30 amps = AWG # 10 wire with 30 amp breaker 40 amps = AWG # 8 wire with 40 amp breaker
No. The 20 amp breaker is probably protecting a #12 wire. Connecting a 40 amp breaker to the 20 amp #12 wire would seriously overload the #12 wire. This means that if the load increased to a full 40 amps the insulation on the smaller size wire would most likely melt off and the wire could short out.
Depends on the wire size used in the circuit. If you use AWG # 14 wire you must use a 15 amp breaker. If it is wired with AWG # 12 wire then you use a 20 amp breaker. If a AWG # 10 wire is used then a 30 amp breaker is required. The breaker protects the wiring from overheating so you must use the proper size breaker for the wire used.
No, 10 gauge wire requires the use of a 30 amp breaker. A 20 amp breaker is only used on 12 gauge wire.
If it is a 30 amp breaker then it is a 240 volt outlet.
You use the correct size breaker depending on the size wire in the circuit. If the circuit is wired with AWG #12 wire use a 20 amp breaker. If it is wired with AWG #14 wire then use a 15 amp breaker.
A dryer requires a 30 amp receptacle. This will be to receive a four blade dryer plug. The wire needed will be a three copper wire #10 cable set with a bare #14 copper ground wire. The breaker will be a two pole 30 amp breaker.
If your question is can you use a #6 flexible SOOW cord and put a 30 amp plug on it, then yes. The breaker that feeds the receptacle that the cord will plug into can be no larger than a 30 amp breaker. What limits the cord capacity to 30 amps is the ratings of the plug on the end of the cord.