10 kW at 220v will use 45.45 Amps. I'd recommend a 60A circuit, with a 60A breaker, but the heater or electric furnace should have "maximum fuse amps" rated on its nameplate. Above all, neverconnect wiring to a breaker that is rated higher than the maximum current capacity of the wire. In the case of 60A, use #6 AWG wire.

The HVAC Veteran

User Avatar

Wiki User

14y ago
This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: Is a 60 amp breaker correct for a 10 kw 220 heat strip?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Continue Learning about Electrical Engineering
Related questions

Can 10-2 wire carry 220 volts?

Yes as long as you use the correct size breaker.


What size breaker for a 8kw heat 7kw cool 240v ac?

P=VI here P=8000 Watts v=220 V I=8000/220 = 37 A so you should use 37A Breaker


How do you test a 220 volt breaker?

You will need a multimeter to check a 220 volt breaker. You should unplug appliances that go to that particular breaker. Use the multimeter at the breaker to check the voltage. If it shows 220, then the breaker is okay. If it doesn't, then the breaker is no good.


Will a 4500 watt element work at all or just trip a 20amp breaker?

A 4500 watt element will work on a 20 amp breaker if it operates at 220 volts or less. It will simply trip the breaker if the load is greater than 20 amps at 220 volts.


Why would plugging in an AC unit in a wall receptacle cause the fuse to blow or breaker to trip?

Is the receptacle a 110 or a 220 outlet? If it's a 110, it needs to be a 220. Are there other appliances, lights, etc. wired on the same outlet? If so, you may have to re-wire so that no other appliances, lights, etc. are wired into the same breaker. Usually the larger appliances such as air conditioners, central heat systems are wired to a separate breaker or fuse.


Do electric dryers require a 220 v plug?

They usually operate at 220 to 240 volts with a 30 amp breaker. So the answer is yes.


Arcing at the 220 volt breaker and hot bus bar?

Phone an electrician urgently


What size breaker is needed for a 220 v hot water heater?

The wattage of the water tank is needed to size the breaker and the wire to feed the tank.


Can you use a 60 amp breaker for a airconditioner with heat instead of two thirty amp breakers?

No. If your AC is currently running on a 30 amp 2 pole breaker, then it is a 220 volt unit. You cannot substitute one 60 amp single pole breaker as you'll only be supplying 110 volts and the AC unit won't work. In fact you could damage it.


What would happen if a 240V breaker was on and someone attempted to turn on the clothes dryer?

Don't understand this question. If the breaker is on, then the dryer would function normally, if the breaker your are referring to is the one for the dryer. If the breaker is off then no function. A dryer runs on 220.


Can you use a range 220 for a dryer 220?

The plugs are different. The prongs are straight on one and angled on the other. The wire and breaker are the same. You can either change the outlet or the cord.


How do you upgrade household wiring from 110 volt to 220 volt?

your house has 220 you must use a 2 pole breaker. your wiring will change ,not a do it your selfer call someone