answersLogoWhite

0


Best Answer

watts = amps x volts
400amps x 480V = 192,000 watts
192,000/1000 = 192KW
You would need 192KW generator at 277/480 <<>> The formula for kilowatts is, kW = I x E x 1.73 x pf/1000. kW = 400 x 480 x 1.73 .90 = 298944/1000 = 298.9 or 300 kW generator.

User Avatar

Wiki User

11y ago
This answer is:
User Avatar
More answers
User Avatar

Wiki User

13y ago

For a 3-phase service that can supply 400A, a 333kVA transformer would be needed. If you aren't planning on using that much power, a smaller transformer can be used. Also, if load is not constant, you can overload Transformers to a degree.

This answer is:
User Avatar

User Avatar

Wiki User

12y ago

A #600 MCM wire with an insulation factor of 75 and 90 degrees C is rated at 420 and 455 amps respectively.

Most 400 amp services disconnects will use parallel wires feeds on each leg to feed the circuit. Parallel conductors will be #3/0

A #3/0 wire with an insulation factor of 75 and 90 degrees C is rated at 200 and 210 amps respectively.

This answer is:
User Avatar

User Avatar

Wiki User

10y ago

The size/mass of the transformer is set by the power that is being put through the transformer. One for 1 kW would be a lot smaller than one for 100 kW.

This answer is:
User Avatar

User Avatar

Wiki User

13y ago

Type your answer here... a very big one

This answer is:
User Avatar

User Avatar

Anonymous

Lvl 1
4y ago

50KVA

This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: What size transformer is needed if you have 30 amps of 480 volts?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Related questions

What size ground wire for a 30 kva transformer?

The size of grounding wire is based on the amperage output of the transformer. The voltage of the transformer needs to be stated. Without this voltage a calculation can not be made. Amps = Watts/Volts = 30000/?.


What size ground wire needed for 75 amps at 208 volts?

#8 copper


How do you size a transformer based on amperage I have a 1 KVA single phase transformer I was told I can only put 4 amps across the secondary. This transformer is 240 volt primary 120 volt secondary?

On a 1kva you have 1000 watts capacity. To fine the current the formula is I = W/E. The secondary side of the transformer has the capacity of 1000/120 = 8.3 amps. In your question you do not put the amps across the secondary you draw amps from it. Using the transformer to its maximum, without overloading it, the primary will be 4.16 amps at 240 volts and the secondary will be 8.33 at 120 volts. &lt;&lt;&gt;&gt; voltage times amps equals wattage


What size wire needed for 25 amps 220 volts for 75 feet?

10 AWG in copper.


What size generator is needed to run a refrigerator?

Depending on size of Fridge. But AVERAGE is 12 volts for fridge, circuit necessity 15 amps 15 amps X 120 Volts=1800 watts minimum...I'm LEARNING myself


What minimum fuse rating is needed for a 12 volt circuit when using one 48 watt bulb?

The formula you are looking for is Watts = Amps x Volts. Amps = Watts/Volts. This comes to 4 amps load. Minimum size fuse would be 5 amps.


What size wire is needed for 6.3 amps 240 volts 50 foot run?

14 AWG is fine for this application.


What size wire to carry 8 amps at 120 volts?

A # 14 copper conductor will be fine to carry 8 amps at 120 volts. This size conductor is rated at 15 amps.


What is the breaker size for a 10 KVA electric heater?

What size breakers are needed for a 30kva transformer 208 volt feed 600 volt out put


How many output amps is a 45 kva transformer?

There is not enough information provided to answer. KVA is short for "Kilo Volt Amperes". That is, thousands of Volt Amps. In order to determine how many Amperes are flowing, you must know at what voltage it is operating. Amperes = 45,000 &divide; volts Bill Slugg


How do you solve for the size of wire when the given is kva?

The V stands for volts and A is amps. If for example you have a 12kVA device and are running off a voltage of 120 volts then Amps = 12000/120 = 100. You then use the calculated amps in a wire size table to get the correct size.


What size breakers are needed for two 500 watt baseboards?

Each baseboard heater will draw a little over 4 amps at 120 volts or 2 Amps at 240 volts. The total number of baseboards on a circuit will draw the sum of these amps. Keep the load under 80% of the amperage rating of the breaker.