some motors, like the one in a dryer, require a nuetral. other 220 volt motors only need the two hot legs.
the size of the wire that you need to run depends on the the amperage of the device/appliance you'll be hooking up to that line. Use #12 wire for 20 amp, #10 for 30 amp, #8 wire for 40 amps and #6 for 50 amps. Hope that helps.
About 660 watts. A hair dryer has a small blower motor and a resistance winding that heats up. The formula is watts = volts x amps x power factor. In the case of a resistive load like the wire that heats up the PF = 1. However, the blower will have a lower PF of about .8.
120 15 amp service ? 210 7 amp service ?
Check the nameplate rating on the door or door frame of your washer, it should tell you the amp rating or the kw rating of the machine. If it only has the KW rating of the machine, simply divide the KW rating by the voltage of the receptacle and it'll give you the current (ampere) rating. Typically, a modern washing machine will draw approximately 7-12 amps. However, anticipate a higher amperage when starting the machine as the machine will draw 1.5X the rated current to start the machine (starting current). Regardless of the amp rating, the NFPA-70 (National Electrical Code) requiresa 20 Amp fuse or circuit breaker; and the circuit for the washing machine must be on its own, dedicated circuit.
Watts, amps and volts are three separate but interrelated electrical units of measure. To find any of the three, you must first know the other two. Since you only provided Watts, one would first need to know Volts before giving you the Amps.
Standard recpt. for house hold is 15 AMPS wired usually with 14 awg, but applicance circutis are 20AMPS wired with 12awg. Dryer rect. are 30AMPs wired with 10 awg and Ovens are 50 Amps wired with 6awg.
Probably not. The reason is the amperage required by the electric range. They typically require 50 amp whereas a dryer normally only requires 30 amp. Therefore, the wiring feeding the dryer is not large enough to support an electric range. Your range should be wired with #6 or 8 gauge wire, whereas your dryer is likely only wired with # 10 gauge which will not carry 50 amps.
Amps are units of current, watts are units of power. Watts are the product of Amps times Volts. Watts = Amps x Volts.
A 30 amp dryer cord is the cord that comes attached to new clothes dryer. It is used to transfer the voltage from the wall receptacle to the dryer appliance. Earlier model dryers used to be hard wired directly from the distribution panel to the dryer. Hard wiring is no longer the case as people wanted to take there appliances with them when they moved from one home to another. New homes are now wired with 30 amp receptacles situated in the wall alcove where the dryer is to be situated. This allows the home owner to plug in the dryer without the hiring of an electrician to legally make the connection. Dryers that have been previously been hard wired can be upgraded with a 30 amp cord kit that can be purchased at any hardware store. Following the instructions included with the kits, any home owner can make the conversion and then connect their dryer into the dryer receptacle.
It may not damage the dryer. But....if the dryer tries to use more than 20 amps, or if anything else is connected to the breaker totaling MORE than 20 amps, the breaker will pop. The breaker disconnects (throws, pops, etc.) if there is too much current being drawn. Too many light bulbs, heaters, stoves, etc. This is designed as a safety so that wires don't melt, fires start and so on. Consult the manufacturer to see if is OK. Or at least look at the label on back to see how many amps it uses. If it's even close to 20 amps, it might be good to have an electrician see about upgrading the breaker/ wiring.
120 V
No.By which I mean: amps and watts are not just different units, they're different TYPES of units. You can't convert amps to watts without knowing the voltage (if you DO know the voltage, multiply volts by amps to get watts).
Amps or amperes
Amps
An average home nowadays has a 200 amp panel. The dryer and stove use 30 and 40 amps and almost everything else is 15 amps.
amps require lots of breathing room, and some high watt/amp units have fans along with the normal ribbed heat sink cases...thats why amps have those fins..to dissipate heat.. :)
60 amps is twice the amount that you need for a household dryer. What you need is a two pole 30 amp breaker feeding a three conductor #10 cable. A dryer needs a neutral wire, hence the three wire cable for a 240 volt device.